Charlie,
The SDS 's I see are not Poco and do not have infinite primary but have a definite ASCC at the primary connection.
Example;
75 KVA , 480V Pri, 208V Sec, 4.6 %Z, 25000A ASCC at Pri,.
By re-writing the Bussmann Point-To-Point method for a second transformer in system, the ASCC at the Sec. terminals would be and using continous hand calculator steps ( ie where * = Multiply, + = add, M+ = memory in, Mr = memory recall, / = divide, 1.732 = 3? multiplier and = = equal: ( the final = is the ASCC at the Sec. terminals.;
Pri ASCC / 100,000 * Pri V * 1.732 * %Z / KVA = + 1 = M+ 1 / Mr = * Pri ASCC / Sec V * Pri V = _____________ Sec ASCC.
( remember to clear calculator before starting the following sequence of steps.)
25000A / 100,000 * 480V * 1.732 * 4.6 / 75 = + 1 = M+ 1 / Mr = * 25000A / 208V * 480V = _____________ Sec ASCC. ( which is 4196.5557 Amperes .
This is a lot LESS than the Pri. ASCC.
gwz2
edit; had some spelling errors.
Remember these are calculator continous steps.