Hi,
Can someone please help me understand the exception from the title?:
215.10 exception 2: The provisions of this section shall not apply if ground-fault protection of equipment is provided on the supply side of the feeder and on the load side of any transformer supplying the feeder.
It's the second part with the transformer that throws me off.
Do both conditions of this exception have to be true in order to use this exception? The way I interpret it is: you don't need GFP on a feeder if further upstream of that feeder (whether the service or another feeder) already has GFP AND that GFP that's upstream is ALSO on the load side of a transformer. Is this correct? Or is it one condition or the other that can trigger this exception?
Can someone please help me understand the exception from the title?:
215.10 exception 2: The provisions of this section shall not apply if ground-fault protection of equipment is provided on the supply side of the feeder and on the load side of any transformer supplying the feeder.
It's the second part with the transformer that throws me off.
Do both conditions of this exception have to be true in order to use this exception? The way I interpret it is: you don't need GFP on a feeder if further upstream of that feeder (whether the service or another feeder) already has GFP AND that GFP that's upstream is ALSO on the load side of a transformer. Is this correct? Or is it one condition or the other that can trigger this exception?