Section 220.84

Status
Not open for further replies.
If I have a building with 50 dwelling units, for example, each one with a load of 80 KVA, I may use PART IV of article 220 and the demand would be 10+70*0.4 what gives me a demand of 38 KVA per unit. After this calculation, can I apply the demand factors in table 220.84 to calculate the feeder of the main meter panel ? Thanks for your help.
 
Continues

Continues

Is it correct to follow with the this calculation
Demand= 1900 KVA or
Demand= 1900 KVA x 0.26 (according with 220.84)= 494 KVA

TX
 
Status
Not open for further replies.
Top