I have a question regarding the Minimum Cover Requirements for underground installations, section 300.5 (C), which states that "Underground cable and conductors installed under a building shall be in a raceway." What exactly does the NEC mean by "under a building"?

Does it mean the raceway must be installed underneath the basement foundation concrete slab? Or can the raceway be installed under a subfloor of the building?

Thanks in advance.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If it's under the on grade slab then it's outside of the building. If it's in the slab then it's within the building.
 