tallgirl
Senior Member
- Location
- Glendale, WI
- Occupation
- Controls Systems firmware engineer
The '08 NEC seems to contradict itself (see (B)(7)), as well as the '08 ROP on the size of the largest backfeed breaker.
My understanding was that if I have a 200A service the size of the largest backfeed breakers was reduced by the sum of the breakers serving loads. A proof, I offer a piece of wire and two OCPDs connected in series by said piece of wire.
If the piece of wire is just a piece of wire, rated for 200A continuous, I can backfeed all 200A from an inverter into the supply. But if I call the piece of wire a "buss bar", at most I can back feed 40A.
What's wrong -- the understand of the section, or the section itself?
My understanding was that if I have a 200A service the size of the largest backfeed breakers was reduced by the sum of the breakers serving loads. A proof, I offer a piece of wire and two OCPDs connected in series by said piece of wire.
If the piece of wire is just a piece of wire, rated for 200A continuous, I can backfeed all 200A from an inverter into the supply. But if I call the piece of wire a "buss bar", at most I can back feed 40A.
What's wrong -- the understand of the section, or the section itself?