Sectioned Equipment

Status
Not open for further replies.

jtp

Member
Location
Iowa
In NEC 310.10(H)5, "Sectioned" equipment bonding reads differently than just equipment bonding. Can someone clear this up for me? What is Sectioned equipment? and the different application of Table 250.122 if Sectioned Equipment?
 

Smart $

Esteemed Member
Location
Ohio
Some multiconductor cables, usually in the larger sizes, will put in three EGC's to reduce the total cross-sectional area of the cable. The combined cross-sectional area of these three EGC's is equivalent to or exceeds the standard 250.122 EGC, i.e. its cross-sectional area.
 

jtp

Member
Location
Iowa
Some multiconductor cables, usually in the larger sizes, will put in three EGC's to reduce the total cross-sectional area of the cable. The combined cross-sectional area of these three EGC's is equivalent to or exceeds the standard 250.122 EGC, i.e. its cross-sectional area.

Thanks, that makes sense . I got hung up on "Sectioned" Equipment.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Thanks, that makes sense . I got hung up on "Sectioned" Equipment.

As Smart stated it's a code permissible way to get several EGC's to make one larger one. Normally paralleling of smaller EGC's to make a larger one is not permitted.
 