Been doing some surfing and was reading of the code questions someone had about cable ties on mc cable. What do you think of the response to the question. Nec doesnt really define 'secure' or 'support'.
g.c. said:Question 1. I seem to be frequently involved in discussions over the use of cable ties as a supporting means for metal-clad cable. Section 330.30 doesn?t clearly state that cable ties can be used as a support method. I am aware that cable ties are clearly defined as an approved method in the following Code locations: 320.30, 334.30, 338.10(B)(b), and 340.10(4). Could you give us your take on this subject? ? G.C.
Answer 1. Article 330.30 of NEC 2002 requires Type MC cable to be supported and secured at intervals not exceeding 1.8 m (6 ft). Article 300.11 also applies and requires cable assemblies to be securely fastened in place. Article 320.30 allows cable ties to be used to secure type AC cable and does not allow cable ties to be used to support type AC cable. Articles 334.30, 338.10(B)(4)(b), and 340.10(4) also reference cable ties for securing but not for supporting cables. Cable ties are specifically mentioned in 2002 Code articles for securing cable type wiring methods but not as the supporting means. ? Gaylen Rogers, CMP-17