IMO yes. But I'm not sure what an inspector would say. I think some would probably say ok and some no.deerhead said:Would a floater piece of uni strut connected to multiple conduits satisfy the code requirement (344.30 (A)) for securely fastening conduit within 3' of a box,etc?
The definition of fastened is: to attach firmly to something else.
I say you are right!!RUWired said:300.11(B)1
(B) Raceways Used as Means of Support. Raceways shall be used only as a means of support for other raceways, cables, or nonelectrical equipment under any of the following conditions:
(1) Where the raceway or means of support is identified for the purpose
I say the uni strut is listed for use of multiple raceways.
Rick
don_resqcapt19 said:It appears that you are using the other raceways to support another raceway via the strut...I see that as a violation of 300.11(B)(1).
As far as I know the strut is not listed for the purpose of supporting anything, but that is not the issue. Unless you provide independent support of the strut you are using the other raceways to support this raceway.RUWired said:Don you don't think the strut is listed for multiple raceways.(or means of support is identified for the purpose)
Rick
don_resqcapt19 said:As far as I know the strut is not listed for the purpose of supporting anything, but that is not the issue. Unless you provide independent support of the strut you are using the other raceways to support this raceway.
deerhead said:Would a floater piece of uni strut connected to multiple conduits satisfy the code requirement (344.30 (A)) for securely fastening conduit within 3' of a box,etc?
It is my opinion that you are using a raceway to support another raceway if you do that.deerhead said:I'm intending this to be in an industrial establishment where multiple rmc's are coming out of a control panel and there is no structural or piece of equipment to attached a rod/strap to the uni strut.
Thanks for all the responses.
frizbeedog said:Agreed.
The strut is a means of support, but not when attached to the conduit only.
The strut must be secured to other than the conduit alone.
Strees and strain added to a conduit system by supporting other conduits.....Not good.
peter said:An empty conduit, in parallel with the others, could be used to support the "flying" piece of strut. Just label it "support".
The loophole is that, even though this piece of UniStrut has to be supported by the structure, there is no clear definition of the quality of this support. Thus even a single strand of grid wire from the strut to the building will do. I don't like it but there you go.
~Peter