I agree 5/8" mud ring is proper for 1/2" Sheetrock. The issue is the depth between the block and the inside of the sheetrock is only 1.5" and the 1900 box/cover/screw combination is thicker than that. We've had level 5 finish jobs where they wouldn't accept the bulge in the rock around the boxes.Then use a 5/8" raised mud ring.
-Hal
Hal, are you implying that the bracket of the plastic bracketed box should be notched out to be flush with the stud or that it will cause a bulge?Bracket boxes are set back to compensate for the thickness of the cover plate and screws which should be flush with the face of the stud. There are times when a box is proud of the stud face and it is noticeable unless the taper levels the area with mud. Good way to PO a fussy GC.
-Hal
That is a very common and accepted practice in Florida.It's been years since I've done residential, but when I did a home that used foam board insulation, the inspector allowed me to use a scrap piece of the NM jacket and loop it around the cable, then drive a cut nail (case hard) through the piece of sheath and into the cinder block. It was quick and easy and secured the cable really nice.
Have you ever sighted a a wall with 1/2" sheetrock. 16" centered studs will show bows between the studs. If it a level built aroundI agree 5/8" mud ring is proper for 1/2" Sheetrock. The issue is the depth between the block and the inside of the sheetrock is only 1.5" and the 1900 box/cover/screw combination is thicker than that. We've had level 5 finish jobs where they wouldn't accept the bulge in the rock around the boxes.
Plastic? What's that??Hal, are you implying that the bracket of the plastic bracketed box should be notched out to be flush with the stud or that it will cause a bulge?
Have you ever sighted a a wall with 1/2" sheetrock. 16" centered studs will show bows between the studs. If it a level built around
here than 5/8" is used.
There is no compensating in normal construction if you mount the box to the stud according to the bracket. It's this special situation where you have to fudge to get the depth right.compensating for the flange of the mud rings.
. Just genuinely confused by this idea of compensating for the flange of the mud rings.
You frame a stud wall. You can use metal studs that are only 1 5/8" deep so you don't lose much real estate. Furring strips are for hacks