The purpose of 300.11(B)(3) is to prevent cables from being attached to the exterior of a raceway. Electrical, telephone, and computer cables wrapped around a raceway can prevent dissipation of heat from the raceway and affect the temperature of the conductors therein. This section also prohibits the use of a raceway as a means of support for nonelectric equipment, such as suspended ceilings, water pipes, nonelectric signs, and the like, which could cause a mechanical failure of the raceway.
However, 300.11(B)(2) does allow the installation of Class 2 thermostat conductors for a boiler or air conditioner unit to be supported by the conduit supplying power to the unit, as shown in Exhibit 300.13. These Class 2 circuits are functionally associated with the branch-circuit wiring method.