I am going to pull my first 400amp parallel underground service entry. Feeding a Seimans single lug meter trough with 2, 200amp discounects. Feeding 2, 200amp panels.
1.) 2 pulls 250 feet in 2, 3 inch PVC conduit
2.) Wire 250 kcm aluminum for the drop 2, hots 1, neutral each pull
3.) Change out the lugs from single to double
4.) Mark and wire correct phases
5.) Grounding 2, G-rouds 6 feet apart bonded with #6 copper then bonded to the meter
Any comments
Thanks