I have a SEL 351S Protective Relay & a Bank of electro-mechanical Panel meters. At Unity PF both the relay & meters read nearly the same.
When I shifted the voltage 120 degrees by moving:
A-Phase Voltage to the relays B-Phase Input
B-Phase Voltage to the relays C-Phase Input
C-Phase Voltage to the relays A-Phase Input
I am at a loss trying to reconcile the relays numbers with the bank of meters. By my thinking this voltage shift should be into LEAD as indicated by the PF Meter sketch. I do not understand how the Watts & Vars add up to be greater than the Watts at Unity. At .5 PF I would expect that the watts & Vars would be equal.
Looks like the Varmeter may have a wiring issue, that is yet unresolved because it is reading low. The electro-mechanical panel meters use 2 currents A & C for measurements. The low reading on A-phase current is a test set anomaly.
When I shifted the voltage 120 degrees by moving:
A-Phase Voltage to the relays B-Phase Input
B-Phase Voltage to the relays C-Phase Input
C-Phase Voltage to the relays A-Phase Input
I am at a loss trying to reconcile the relays numbers with the bank of meters. By my thinking this voltage shift should be into LEAD as indicated by the PF Meter sketch. I do not understand how the Watts & Vars add up to be greater than the Watts at Unity. At .5 PF I would expect that the watts & Vars would be equal.
Looks like the Varmeter may have a wiring issue, that is yet unresolved because it is reading low. The electro-mechanical panel meters use 2 currents A & C for measurements. The low reading on A-phase current is a test set anomaly.