Up in my neck of the woods it's pretty common that switched outlets are wired with #12 with a 15 amp receptacle on a 20 amp breaker, and a 15 amp toggle controlling it. Does 404.14 (F) forbid this? Im thinking a 20 amp switch is now required. What do you guys think?
Other than this scenario do you only use a larger switch to fit the required load?