According to NFPA 310.60(B)(1) "Where more than one calculated or tabulated ampacity could apply for a given circuit length, the lowest value shall be used
"Exception: Where two different ampacities apply to adjacent portions of a circuit, the higher ampacity shall be permitted to be used beyond the point of transition, a distance equal to 3.0 m(10ft) or 10 percent of the circuit length calculated at the higher ampacity, wichever is less"
I'm calculating the required conductor for feeding a MCC 100 m (328 ft) away from a power transformer. The cable run is divided in three sections. The first one starts in the transformer and is made on cable tray for 80 m., then the second section is made in bank duct for 8 m., and the last section is run on cable tray again. My question is if the 8 m. of run in the bank duct makes me select the lowest ampacity value, having in mind that 8 m is less than the 10% of the whole circuit length.
Thank you.
"Exception: Where two different ampacities apply to adjacent portions of a circuit, the higher ampacity shall be permitted to be used beyond the point of transition, a distance equal to 3.0 m(10ft) or 10 percent of the circuit length calculated at the higher ampacity, wichever is less"
I'm calculating the required conductor for feeding a MCC 100 m (328 ft) away from a power transformer. The cable run is divided in three sections. The first one starts in the transformer and is made on cable tray for 80 m., then the second section is made in bank duct for 8 m., and the last section is run on cable tray again. My question is if the 8 m. of run in the bank duct makes me select the lowest ampacity value, having in mind that 8 m is less than the 10% of the whole circuit length.
Thank you.