I am still sticking with what I said earlier - it is intended to be connected to 220 volts or 380 volts. At 220 volts it will draw 4 kW, at 380 volts it will draw 6 kW. My question was which voltage will you be utilizing? You need to know that before you will know which power rating to use to find circuit amps.check the oven name plate
I am still sticking with what I said earlier - it is intended to be connected to 220 volts or 380 volts. At 220 volts it will draw 4 kW, at 380 volts it will draw 6 kW. My question was which voltage will you be utilizing? You need to know that before you will know which power rating to use to find circuit amps.
Be careful, in Europe a comma is a decimal point. It could be 6.4 KW. ...
Be careful, in Europe a comma is a decimal point. It could be 6.4 KW.
And the ratios 380/220 vs 6/4 don't really jive, either. If it draws 4@220, I'd expect closer to 7@380.
But I struggle to visualize how a combination of elements would be connectable for the same KW at both of those voltages. :?
A connection diagram would be helpful - if the connection is identical for both voltages, then you are right! :thumbsup:
380/sqrt3 = 220
same v either way
1 ph 220 l-n, 1 ph is paralleled to L1 and L2
3 ph 380/sqrt3 x 2 phase-neut, one to each L1 and L2
15 Ohm elements x 2 (I looked at the manual earlier)
220/15= 15 a per element
if 1 ph 35 a 1 pole
if 3 ph 20 a 2 pole
Note: since the power is 6.4 KW, so for single phase the current will be I= 6400/220 = 29 Amps L-N, 1 Ph is paralleled to L1 and L2
For three phase : 6400/1.73 x 380 = 10 amperes
but You multiplied by a factor 2, is this because of two neutral lines?
Note: since the power is 6.4 KW, so for single phase the current will be I= 6400/220 = 29 Amps L-N, 1 Ph is paralleled to L1 and L2
For three phase : 6400/1.73 x 380 = 10 amperes
but You multiplied by a factor 2, is this because of two neutral lines?
Not that other reply was wrong but another way to look at it -Note: since the power is 6.4 KW, so for single phase the current will be I= 6400/220 = 29 Amps L-N, 1 Ph is paralleled to L1 and L2
For three phase : 6400/1.73 x 380 = 10 amperes
but You multiplied by a factor 2, is this because of two neutral lines?
Not that other reply was wrong but another way to look at it -
you are not connected to all three phases, if you were and 6400 was your total kVA, then that would be correct.
What you have is two 3200 watt elements that operate at 220 volts each. Connect them to 380 volt wye with two phases and a neutral and they still see 220 volts across each element because of the phase angle. Current will be 3200/220 = 14.55 amps on each phase conductor, because of the 120 degree phase angle the neutral will also carry approximately same current level.