Yes, I suspect this is at the heart of your issue. That switch only has a utilization category of AC-21, which is for resistive loads only. It has no motor loading rating listed for it at all, or if it does, Siemens doesn’t even bother to list it. Opening up an inductive load such as a 128.5kW motor, while running, is very hard on switching devices. So in selecting the device you must do one of two things:
1. Select a switching device with a kW motor load rating at or greater than your motor load, or
2. ENSURE in your design that the switch is used only for isolation, which means another properly rated device, such as a contactor, will ALWAYS open the motor circuit BEFORE the switch main contacts open. One thing I see happen is that the system may have originally been designed that way, but over the years modifications and repairs have been made. The result is that the contractor is gone, or the coil circuit is no longer tied to six contacts in the isolation switch (or those contacts have welded), and now the isolation switch is opening under load.