Hey everyone,
I know I've been asking a lot of questions today, so thank you everyone for the responses. I am working on a power systems study for an assisted living facility and the standby generator feeds an ATS switch that feeds a main lug only switchboard that is supporting roof top and DOAS units. The ATS switch is labeled equipment branch. The breaker that feeds the automatic transfer switch is rated for 600 amps and it does not coordinate with a 450 amp breaker located on the main lug only switch board down stream. This was a bad design on the engineers part. My question is am I required to selectively coordinate loads on the equipment branch or is selective coordination only required for life safety loads?
Best Regards
I know I've been asking a lot of questions today, so thank you everyone for the responses. I am working on a power systems study for an assisted living facility and the standby generator feeds an ATS switch that feeds a main lug only switchboard that is supporting roof top and DOAS units. The ATS switch is labeled equipment branch. The breaker that feeds the automatic transfer switch is rated for 600 amps and it does not coordinate with a 450 amp breaker located on the main lug only switch board down stream. This was a bad design on the engineers part. My question is am I required to selectively coordinate loads on the equipment branch or is selective coordination only required for life safety loads?