Cannotlogin
- USA
- Technician
It is interesting that they say provide "selective coordination" per NFPA 99, when NFPA 99 only requires coordination and not selective coordination.
The difference being that selective coordination is down to time "zero" while coordination is only down to 0.1 seconds. The coordination rule is much easier to meet, and your breakers probably would work for that...probably won't for selective coordination.
It's not likely that a QO20 will coordinate with an upstream QO40.
That's a really good point, and it's illustrated in the attached TCC. The instantaneous portions overlap such that selective coordination is not apparent. But the referenced literature shows the two breakers coordinate selectively up to 10kA. (Table 4, p.11)You typically cannot see selective coordination, for small breakers, by using trip curves unless the fault current is below the Instantaneous pick up point. You need to go to the published tested combinations from each manufacturer.
You would have to look at the instantaneous part of the trip curves and the available fault currents. It is much easier and cheaper to coordinate at 0.1 seconds than at zero seconds.Is 0.1 realistic for all faults or does it just takes reasonably probable faults into account?
There is a bit of slop in the way TCCs are actually drawn. Breakers often perform far faster, in the Instantaneous region, than the TCC shows, due to improvements in components and design Historically the industry shows the worst case performance on their TCC even if it covers only .05% of the breakers which might be sold (things liked switched neutral and auxiliary switches could impact breaker performance. By putting breakers in series it is possible to take advantage of a specific breaker configuration's speed as well as any dynamic impedance that may be present at lower fault currents.Any idea why? Thats just really confusing.
They coordinate because of dynamic resistance which does not show up on a TCC...it does in tested combination data.
Dynamic resistance?
Even if you got rid of the 40 amp breaker on the load side of the ATS, it is not likely that the branch breakers in the panel would coordinate with the upstream 40 amp devices.Does anyone else object to the main breakers on the load side of the ATS's?
How will anyone ever find a 40A breaker on the load side of a LS-ATS that will coordinate with either 40A breaker on the line side of LS-ATS? I suppose it could be done if 40A electronic trip breakers are available. But think of the cost it would add. And why?
Same with the 400A switch.
Eliminate the mains on the load side of the ATS's.
You need to remember that 700.32 and 701.32 were written by someone who works for Bussmann....and their fuses work just fine for selective coordination applications.