A very interesting point you make about ground fault!
A very interesting point you make about ground fault!
But keep in mind that we are only talking about Emergency Systems. As such, on the secondary side of the ATS's, GF is not permitted. That said, if we were feeding a 1000A plus ATS, there'd we'd have Ground Fault and if I understand your point correctly, this breaker with ground fault would never see a ground fault down stream of the 1:1 transformer on the secondary side of the ATS's. In this case, I would think my colleague envisions multiple ATS's, (30 to 45kVA) like one on every floor feeding the Life Safety and Critical system (we primarily do hospitals), etc. Since we don't want these branches to trip on ground fault and since we don't want to have a 1000A plus breaker upstream of the ATS tripping on ground fault and shutting down a very large section of the hospital, I wonder if the 1:1 transformer is actually providing us a relevant service?