Selective Coordination

Status
Not open for further replies.
Are selective coordination requirements of elevator, emergency and legally required systems per NEC 620.62, 700.27 and 701.18 being enforced in other parts of the country because I was told it is not.
 

iwire

Moderator
Staff member
Location
Massachusetts
Nate Scott said:
Are selective coordination requirements of elevator, emergency and legally required systems per NEC 620.62, 700.27 and 701.18 being enforced in other parts of the country because I was told it is not.

Enforced or Adopted?

If an area did not adopt those sections or made amendments to them that is one thing.

If an area simply does not enforce an adopted rule and the designer / installer decides not to follow the adopted rule due to lack of enforcement that designer / installer will forever be 'on the hook' for that violation.
 

RB1

Senior Member
I have heard that some jurisdictions are negating the first .10 second for coordination of molded case circuit breakers. Does anybody know if there is any truth to this?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
RB1 said:
I have heard that some jurisdictions are negating the first .10 second for coordination of molded case circuit breakers. Does anybody know if there is any truth to this?

Wisconsin has been enforcing the 2005 NEC as written. If the legislature approves the proposed amendment, when Wisconsin adopts the 2008 NEC there will be a state exception for times of 0.1 sec or longer.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
RB1 said:
I have heard that some jurisdictions are negating the first .10 second for coordination of molded case circuit breakers. Does anybody know if there is any truth to this?

And I've heard that others are negating the first 0.01 seconds.

It's really hard to coordinate circuit breakers below that level. I guess they want us to go back to using fuses everywhere.

IMO, this is one of those code sections that sounds great on paper, but just isn't practacle in the real world.

Steve
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
steve66 said:
I guess they want us to go back to using fuses everywhere.

Fuse "ratio charts" are only good for that specific manufacturer, as soon as you put in a different brand fuse (which of course never happens:smile: ) you loose your guarantee of coordination.
 