A down stream 13.8kv line fault caused A and B phase cutouts to blow tasked with protecting a 23kv-13.8kv auto transformer bank.
A bit of info on the scheme going from back to front: 23kv incoming line, 100K primary fuse links, 3 1254kva 13.2kv-7.9kv step down auto transformers, VT bank for the recloser control, microprocessor controlled recloser as part of a loop scheme, 13.8kv outgoing.
{It appears as though the 23kv upstream recloser's fast curve (not pictured here) can "reach" through the step down bank and clear for a fault on the 13.8kv side, while the upstream's slow curve blows the bank cutouts on A and B phase. The 13.8kv recloser pictured here appears to act merely as a voltage sectionalizer for loss of the incoming 23kv. Not sure if the prior is deliberate or inadvertent}
My question is, could this ever be intended? Should the bank cutouts be changed to 140 or 200K? Is coordiantion with the recloser pictured here practically realistic or worth considering? Shouldn't the 13.8kv recloser do all over current tripping for the 13.8kv side and not the upstream 23kv devices?