406.10 shall comply with 250.146 simple ? 250.156(B) states contact devices
or yokes designed and listed as self grounding shall be permitted in conjunction with the supporting screws to establish the grounding circuit between the device yoke and flush type boxes.
okay in 250 it talks about clean surfaces,metal to metal contact,in conjunction with.
my contention is if outlet is in contact with flush box , good , but if outlet is not in contact with box i.e. spaced by vinyl wall protecter a jumper should be installed as in 250.146
outlet is self grounding with flush box with no contact except screws in upstate New York
If i'm mistaken a wall of shame will be started with this.
or yokes designed and listed as self grounding shall be permitted in conjunction with the supporting screws to establish the grounding circuit between the device yoke and flush type boxes.
okay in 250 it talks about clean surfaces,metal to metal contact,in conjunction with.
my contention is if outlet is in contact with flush box , good , but if outlet is not in contact with box i.e. spaced by vinyl wall protecter a jumper should be installed as in 250.146
outlet is self grounding with flush box with no contact except screws in upstate New York
If i'm mistaken a wall of shame will be started with this.