Sensors in Class II Div 2.

Status
Not open for further replies.

ryanb74

New member
Location
United States
I have a project that I am working on that will be installed in a Class II Div 2 location. I have two dust-tight sensors with quick disconnects (Turck M12). The sensors are rated at 24VDC and are solid-state. My interpretation of the code is that the cabling would not be allowed, but could the sensor be used if connected directly to conduit?

Thanks,
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
I have a project that I am working on that will be installed in a Class II Div 2 location. I have two dust-tight sensors with quick disconnects (Turck M12). The sensors are rated at 24VDC and are solid-state. My interpretation of the code is that the cabling would not be allowed, but could the sensor be used if connected directly to conduit?

Thanks,
I don't quite understand what gave you the impression that cables were unacceptable. There are several methods mentioned in 502.10(B) including cross-references ultimately leading to 502.140.

That said, connecting directly to conduit would be dependent on manufacturer's instructions.
 
Status
Not open for further replies.