sceepe
Heres the deal, regular old dry type 480V pri, 208 secondary. System bond jumper between Xo and xfmr egc terminals. Assume that you have a proper electrode system and electrode condutor from the xfmr's egc terminal.
Questions:
1. Do you size the ground wire to the secondary side panel based on 250.66?
2. Is this a equipment grounding conductor or an equipment bonding jumper?
3. Say you have parallel feeds to the secondary side panel, do you still size the ground to the panel based on 250.66 in which case the grn in each raceway is based on the total circular mills of all conductors per phase. -OR- do you size the ground using 250.66 based on the size of the conductor in one raceway ignoring note 1????
Maybe this is would be more clear: 112.5 KVA 480 to 208 dry type feeds a 208V panel with a 400 amp main breaker. The system bonding jumper is installed at the transformer. The panel is supplied by 2 sets of 3/0 conductors and a ground. What size is the ground (#4 or #2).
I think #4 is correct based on 250.102(C), but I can't explain why 250.102(C) tells you to size it differently than any other time you use 250.66.
[ June 08, 2005, 04:45 PM: Message edited by: sceepe ]