- Location
- Tennessee NEC:2017
- Occupation
- Semi-Retired Electrician
I know that at a dwelling you could run SE conductors to a separate building without having a disconnect on the main building.
What I'm questioning myself on is this. If it is not a dwelling, and you run SE conductors to a separate building, you have to have a disconnect for the separate building at the main building. My confusion is, do you also have to have a disconnect for the main building on the outside in order to meet the requirements for grouping the disconnects?
Or can the disconnect for the main building be inside at the panel and only the separate building needs the disconnect outside at the main building.
Maybe this will clarify what I'm asking in case I didn't word the question right.
There is currently a building undergoing a remodel and they want to upgrade their service from 200A to 400A.
They want to come off the meter with two sets of SE conductors.
One set to a 200A panel in the main building and the other to another 200A panel in a separate building.
How does this need to be done?
What I'm questioning myself on is this. If it is not a dwelling, and you run SE conductors to a separate building, you have to have a disconnect for the separate building at the main building. My confusion is, do you also have to have a disconnect for the main building on the outside in order to meet the requirements for grouping the disconnects?
Or can the disconnect for the main building be inside at the panel and only the separate building needs the disconnect outside at the main building.
Maybe this will clarify what I'm asking in case I didn't word the question right.
There is currently a building undergoing a remodel and they want to upgrade their service from 200A to 400A.
They want to come off the meter with two sets of SE conductors.
One set to a 200A panel in the main building and the other to another 200A panel in a separate building.
How does this need to be done?