Sparky2791
- Northeast, PA
- Electrical Design
Scenario:
Existing building has a 1200A 120/208V 3 phase service. The GES is already established at the existing building.
New addition will have a new stair tower that attaches to the existing building making it all one building. The existing building steel will not attach to the new building steel.
The new addition will be fed with a 400A feeder via a 400A breaker in the existing 1200A service distribution panel.
Question:
Since existing and new building steel are not mechanically connected, does the building steel for the new addition need a bonding jumper from the existing building steel otherwise the new addition would be considered a remote building and therefore 250.32 (B) would apply? Also, if it is considered a remote building the EGC would be sized on 250.122 not 250.66 in the 400A feeder according to that section.
Question: