Im an Air Force electrician in Iraq, and Im trying to figure out if what is installed is safe and correct. We have 6 facilties in a row that are fed by the same Main Distribution Panel. The MDP is fed by a 1200A Double throw switch, which is in turn fed by 2 800kw Generators that only run one at a time. From 1200 amp MDP, it then supplies each building a 250 Amp service. No grounds were pulled from the MDP to each building. They drove ground rods and bonded the EGC to the neutral bus in the panel inside each building. Is this correct? Also, the generators and double throw were bonded to a single ground rod, and the MDP has its own ground rod. These two ground rods are also bonded together, and they are about 10 ft apart. They also have the neutral and ground bonded at the transfer switch, and then again at the MDP....Is any of this right? Any help would be appriciated!....SSgt Kincaid