S shamilton New member Dec 7, 2017 #1 Hi,I'm running a separate feed to a pole barn. The meter can must be within 3' of pole, can I run three wires from can to pole barn and bond in the distribution panel and drive 2 ground rods. Thanks, Scott
Hi,I'm running a separate feed to a pole barn. The meter can must be within 3' of pole, can I run three wires from can to pole barn and bond in the distribution panel and drive 2 ground rods. Thanks, Scott
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Dec 7, 2017 #2 Do you mean a multiwire branch circuit. 1 neutral and 2 hots?
publicgood Senior Member Location WI, USA Dec 7, 2017 #3 I am assuming this feed is via utility, not other on-site distribution. Pending review of local utility requirements, yes.
I am assuming this feed is via utility, not other on-site distribution. Pending review of local utility requirements, yes.
kwired Electron manager Location NE Nebraska Occupation EC Dec 7, 2017 #4 Where is service disconnecting means? Is your mentioned "meter" essentially the utility supply or is there a service disconnect ahead of it somewhere?
Where is service disconnecting means? Is your mentioned "meter" essentially the utility supply or is there a service disconnect ahead of it somewhere?