Separate derived system 480 to 240/120 transformer grounding

Status
Not open for further replies.

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Going thru grounding/bonding videos and i have a question concerning transformers and a common instance in my factory 480VAC Y input Use 2 hots and ground to make 120v/240v single phase system
480VAC feed from MCC 3 wire (no neutral) from breaker.
2 of 3 hots used for transformer primary and ground.
Ground from MCC breaker would be only ground wire.
Run 4 wire to 120v/240v panel from transformer secondary (ground and neutral joined at transformer.

Question In the videos it generally shows at transformer secondary some form of electrode added is this necessary?
 
May not be necessary but it's required.
Thats how i seen it from videos.
I'm in a 100-year-old factory cement floors I-beam construction can I use the I-beam as the grounding electrode?
 
If it meets the criteria of 250.52 then you can.
Thanks i have been looking there the beams are bolted to cement so i think .52 may not apply. But 250.68(C)(2) may. It is tough without knowing whats in the concrete
 
Thanks i have been looking there the beams are bolted to cement so i think .52 may not apply. But 250.68(C)(2) may. It is tough without knowing whats in the concrete
Might be a opportunity of proving 25 ohms?
 