Separate disconnects required for two small variable speed pumps?
greenspark1
New England
I have two 0.68HP 120V variable speed pumps, like these, on a single branch circuit. They each have an integral controller. The electrical panel is in the same room (within sight). Do I need a separate snap switch for each motor/controller, or can I just use the circuit breaker as the disconnect? 430.102 (A) says yes I need separate ones and I have yet to find an exception, but I've never seen separate disconnects in any installations and it seems like overkill for these tiny pumps. I often see 3-5 small circulator pumps on one branch circuit with no additional disconnecting means. Thanks for any feedback.
I agree it is overkill.
I think that the code requires it.
Are they .68 HP or .68 amps?
.68 HP (somewhere between 1/2 and 3/4 hp) is getting to the point where you would only have one motor per 15 or 20 amp 120 volt circuit in the first place.
Otherwise if less then 1/8 hp 430.109(B) would allow the branch-circuit overcurrent device to be permitted to serve as the disconnecting means. and doesn't mention whether it need be within sight or any other conditions.
Thanks for the replies. They are rated 0.027-0.68HP, 2.2-6A max @ 120V. If they are under 1HP, per 430.53(A), they can share a branch circuit.
Can they share a disconnecting means?
If you think its overkill, submit a code proposal. Its very easy to do so. Where do you draw the line in the sand? 1/2 hp? 1/4 hp?
What about using a cord and plug connection? Sometimes it's easier to simply install a duplex receptacle, then put a cord on each pump and plug them in
It needs to comply with 400.7 and 400.8. Cord and plug is allowed to be a disconnecting means, but the item must still be permitted to be cord and plug connected.