I would ask to pull just one EGC in each raceway.
On side note. How does pulling ONE EGC in one conduit with multiple circuits take care of the grounding of all the circuits?
On side note. How does pulling ONE EGC in one conduit with multiple circuits take care of the grounding of all the circuits?
(C) Multiple Circuits. Where a single equipment grounding
conductor is run with multiple circuits in the same raceway,
cable, or cable tray, it shall be sized for the largest overcurrent
device protecting conductors in the raceway, cable, or cable
tray. Equipment grounding conductors installed in cable trays
shall meet the minimum requirements of 392.10(B)(1)(c).
My suspicion is that the intent is to have an equipment grounding conductor in the conduit not multiple equipment grounding conductor's. I would verify this with the engineer.
My money is on exactly what is written, a separate EGC for each circuit.
My money is on exactly what is written, a separate EGC for each circuit.
But is pointless as NEC will require you tie them all together in every box (other than pull boxes with no splicing),as well as bonding to the box if metallic, effectively making them one conductor anyway, true isolated grounding conductors being the exception to this rule.
Might depend on the client and what current relationship I may have with them. Regular client that would happen get a spec like that - very well may question the designer. Most my regular clients I am the designer though, but there are engineered projects sprinkled in here and there.Regardless of all of that it says "provided dedicated equipment grounding for each circuit" which is exactly how I would estimate and install it. If that's what they're paying for then why argue unless of course you want to try and save the client some money.
Triggering the rules against paralleling small conductors, making the spec non-code-compliant.But is pointless as NEC will require you tie them all together in every box (other than pull boxes with no splicing),as well as bonding to the box if metallic, effectively making them one conductor anyway,
Triggering the rules against paralleling small conductors, making the spec non-code-compliant.
310.10(H) Conductors in Parallel.
(1) General. Aluminum, copper-clad aluminum, or copper
conductors, for each phase, polarity, neutral, or grounded
circuit shall be permitted to be connected in parallel (electri‐
cally joined at both ends) only in sizes 1/0 AWG and larger
where installed in accordance with 310.10(H)(2) through
(H)(6).