I've received the final approved plans for an upcoming job that involves upgrading a service.
Existing is 600A 120/208; we have to add another 200A 120/208 disconnect (and interior panel), trench new service conductors from xfrmr pad through existing CT can.
customer/poco doesn't want to replace existing CT cab or disconnect and have a single 800A.
anyhow, the city required the engineer to spec two new electrodes connected to the 200A disconnect w/ #4cu, and also run #4cu to building steel and water lines.
I sent the chief plans examiner an email questioning this (since it was he that required it) -
He argued that we have two services with a common meter. Ok, so the code i cited still applies; he disagrees.
Anyway, not going to argue it. When the inspector turns it down, we'll make necessary changes and bill as a change-order.
I had concerns about using the #4 paralleling with the 600A's bonding connections that are already in place. Plans examiner said it doesn't matter, we're going to do it his way. Anyone else think I'm wrong or know of a code I've missed somewhere?
Existing is 600A 120/208; we have to add another 200A 120/208 disconnect (and interior panel), trench new service conductors from xfrmr pad through existing CT can.
customer/poco doesn't want to replace existing CT cab or disconnect and have a single 800A.
anyhow, the city required the engineer to spec two new electrodes connected to the 200A disconnect w/ #4cu, and also run #4cu to building steel and water lines.
I sent the chief plans examiner an email questioning this (since it was he that required it) -
250.58 Common Grounding Electrode. Where an ac system
is connected to a grounding electrode in or at a building
or structure, the same electrode shall be used to ground
conductor enclosures and equipment in or on that building or
structure. Where separate services, feeders, or branch circuits
supply a building and are required to be connected to a
grounding electrode(s), the same grounding electrode(s) shall
be used.Two or more grounding electrodes that are bonded together
shall be considered as a single grounding electrode
system in this sense.
He argued that we have two services with a common meter. Ok, so the code i cited still applies; he disagrees.
Anyway, not going to argue it. When the inspector turns it down, we'll make necessary changes and bill as a change-order.
I had concerns about using the #4 paralleling with the 600A's bonding connections that are already in place. Plans examiner said it doesn't matter, we're going to do it his way. Anyone else think I'm wrong or know of a code I've missed somewhere?