Separate grounding system

Status
Not open for further replies.

physis

Senior Member
Re: Separate grounding system

If you have a problem with computers it's very unlikely that some kind of exotic grounding system will fix it.
 

ryan_618

Senior Member
Re: Separate grounding system

250.54

Let me edit this for clarity. You still need an effective ground fault current path for the equipment, as per 250.4(A)(5). What I am trying to say is that you could drive ground rods near your equipment and tie to them, but whether you like it or not, you would still be ultimatley tied into the service grounding electrode system through the equipment grounding conductor.

[ May 11, 2005, 08:21 PM: Message edited by: ryan_618 ]
 

pierre

Senior Member
Re: Separate grounding system

You may also be thinking of 250.146(D). In some instances, some will install this conductor all the way back to the service through some panels, without bonding to the enclosures of those panels. This is permitted, as long as you still have a system equipment grounding conductor installed.
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Separate grounding system

Originally posted by gregorsc:
What code section permits a separate grounding system for a computer system?
Point blank answer, none. To do so would make your problems (noise) worse, and put people and equipment in great danger.
 