Re: Separate NEC Residential Code?
I listed 9 differences between the 2003 IRC electrical chapters and the 2002 NEC.
1) E3303.3 of the IRC requires all materials to be listed and labled. The NEC does not require labeling and listing of everything, nor could this be done.
2) E3502.4 requires all systems to be 3-wire 120/240 volts, single phase with a grounded neutral. What about "network", two phases of a 208Y/120 system?
3) E3502.2 allows only the optional compution to be used in computing the size of a service. Why can't the standard method be used?
4) Note c to Table E3503.1 specifies support distances on GECs, where the NEC requires only "securely fastened" (250.64(B)).
5) Table E3503.1 does not allow the use of cable armor for the protection of the GEC. NEC 250.64(B) allows this.
6) The IRC does not detail the bending radius for the following types of wiring methods, where the NEC does: AC, MC, USE, UF, IMC, RMC, FMC, RNC, LFC, EMT, ENT. (E3702.5)
7) E3702.4 requires all cables smaller than 2 #6 or 3 #8 (NM, MC, SE, and UF) to be run on running boards or in bored holes when installed in unfinished basements. The NEC only requires this for NM, SE, and UF cables.
8)The IRC does not allow Concealed knob and tube wiring, while the nEC does. (E3701.2- 394.10)
9) E4104.3 of the IRC has elevated the FPN following 680.26(A) to the status of code.