Separate Neutrals

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Tricking situation here. THe job called for ALL EMT but then we got MC cable approved in concealed locations.
Reading this note would you say 12/3 MC( shared neutral) would be allowed for 120v lighting and power?
 

Attachments

  • Screenshot 2023-05-09 133918.jpg
    Screenshot 2023-05-09 133918.jpg
    133.6 KB · Views: 18
Since you had to ask permission once, that's probably who you should ask. But to me, the answer would be yes, it's okay. Because I don't see a meaningful difference between 'raceway' and 'cable'. That's how I'd ask the question: "Where it says raceway can we also apply that to cable?"
 