Separate power sources in cable tray

Status
Not open for further replies.

bwilder12

Member
Location
Norman,Ok,USA
Can anyone help me? We are on a job and we have been asked to install cables in a cable tray from two separate power sources. What I mean is they have two diferent co ops. So it would 480 volts from both but from two different transformer banks. Is this a code violation?
 
Can anyone help me? We are on a job and we have been asked to install cables in a cable tray from two separate power sources. What I mean is they have two diferent co ops. So it would 480 volts from both but from two different transformer banks. Is this a code violation?
No.
 
NEC does not require you, IMHO, to distinguish two different power sources as long as they are the same voltage system. But I would make sure they do not get confused.

Tapatalk!
 
NEC does not require you, IMHO, to distinguish two different power sources as long as they are the same voltage system. But I would make sure they do not get confused.
I disagree. Exactly how will depend on whether they are service, feeder, or branch circuit conductors [e.g. 230.2(E)].
 