In energizing an ATS whereas:
1) The normal feed is connected to the service (w/o standby emergency power) in which load is located (blbg #1).
2) The emergency feed is connected to the standby emergency generator utilized to back-up an adjacent building (bldg #2) which is served by a separate utility service:
The common of the ATS (load feeder) is to run in existing conduit occupied by other branch circuits from bldg #1. So, as long as there is service continuity, the commom of the ATS and the existing branch circuits are on the same service.
On emergency, the commom of the ATS is "live" from back-up generator in blg#2, but the branch circuits from bldg #1 are "dead".
Would this comply with 700.9 requiring "...wiring from an emergency source or emergency distribution overcurrent protection to emergency loads shall be kept entirely independent of all other wiring and equipment..."