So that I can be sure I understand the responses to the "Separate Building-Minimum Feeder" post correctly (and a couple of other questions)...
I have a premanufactured, skid mounted, chemical metering pump and chemical storage tank installed inside CMU "walls" with a open steel grate "roof" and a chain link "door" for vandal protection.
The skid is feed from an adjacent building's lighting panel with a single 15A 120V circuit and EGC. The circuit feeds the control panel which has a circuit breaker to disconnect the unit inside the control panel door.
No grounding electrode is needed, correct? (250.32 (A) Exception)
Does the chain link door and steel grate roof require grounding? I don't feel they meet the requirements of 250.4 (A) (4) because they are "not likely to become energized".
Is an external disconnect switch required because the means of disconnection is not readily appearent inside the local control panel?
Thanks!
Jim
I have a premanufactured, skid mounted, chemical metering pump and chemical storage tank installed inside CMU "walls" with a open steel grate "roof" and a chain link "door" for vandal protection.
The skid is feed from an adjacent building's lighting panel with a single 15A 120V circuit and EGC. The circuit feeds the control panel which has a circuit breaker to disconnect the unit inside the control panel door.
No grounding electrode is needed, correct? (250.32 (A) Exception)
Does the chain link door and steel grate roof require grounding? I don't feel they meet the requirements of 250.4 (A) (4) because they are "not likely to become energized".
Is an external disconnect switch required because the means of disconnection is not readily appearent inside the local control panel?
Thanks!
Jim