Q1. We have two or more 13.2kV delta primary, 480/277V, 3-phase, 4-wire wye solidly grounded transformers associated with unit substations tied together with tie circuit breakers. All circuit breakers including main and tie circuit breakers are 3-pole. Each unit substation transformer is solidly grounded locally and is a separately derived power source. This required that the neutrals from all unit substations tied together via tie circuit breakers be connected together resulting in multiple grounding of neutrals – once at its source and next at the other source via neutral bus. Is this code compliant?
Q2. We are planning to install Partial Differential Ground Fault Protection schemes to account for all the ground current flowing back to the source via different parallel paths created by multiple grounding of neutrals during a ground fault condition, so that the faulted section can be isolated quickly. Will this protection scheme make the above electrical system code compliant?
Q4. Should we install 4-pole main and tie circuit breakers to prevent multiple grounding of neutrals instead?
Ajoy D.
Q2. We are planning to install Partial Differential Ground Fault Protection schemes to account for all the ground current flowing back to the source via different parallel paths created by multiple grounding of neutrals during a ground fault condition, so that the faulted section can be isolated quickly. Will this protection scheme make the above electrical system code compliant?