The system was designed by someone who chose both neutral switching and non-switching transfer switches. The argument now is does the generator switchboard require a connection to the building GES via a GEC and a bonding jumper when some of the transfer switches have solid neutrals.
Following the others, with different phrasing:
It doesn't matter. The design/installation is screwed up. Installaing additonal GEC/bonding jumpers does not change that.
Install additional - system screwed up
Don't install additional - system screwed up
I suspect this is one of those where, "it is what it is" no one will pony up the money to fix. So the job is to justify - code interpretation; or come up with a low budget fix that allows management to say, "it is okay now".
Assuming 480V grounded Wye: With just the generator driving this, the system is 1500FLA and up in the 10KA - 15KA ASSC. That is absolutely classic for slow trpping CBs - maxium arcflash, maxium equipment damage. Once you start putting your name on the system changes, you are the engineer of record.
I wish I had some bright ideas for you - I don't.
Just curious: Is there an N-G bond at the generator?
edit to add: This is way above a design by code requirements.
ice