I need a little help here. I am designing for a primary metered client who currently has an ungrounded 480VAC 3ph 3W delta system installed circa 1985 in one part of the plant. A 1500kva transformer, located outside, feeds two disconnects, grouped in a single room. Currently there are 3x500 ungrounded conductors in metallic conduit feeding one disconnect and 2x500 ungrounded conductors in metallic conduit feeding the other disconnect. There are no grounded conductor connections of course - just feeders motors and lighting transformers. All good here.
We are replacing the 1500 kVA transformer, and I would like to change this system to a grounded system. Because they are primary metered, this is a separately derived system (not a service). The source and the first disconnect(s) will be in separate enclosures. I'd like to install the system bonding jumper in the transformer, outside, and run the supply side bonding jumpers to the disconnects (with the ungrounded conductors).
I remember an AHJ telling me once - probably related to a service - that the grounded conductor had to be brought to the first disconnect.
We are on the 2017 NEC and I do not see any requirement to bring the grounded conductor to the first disconnect for this installation. Am I correct? Besides - what would it do there, be ready in case someone needed it in the future?
Thanks!
We are replacing the 1500 kVA transformer, and I would like to change this system to a grounded system. Because they are primary metered, this is a separately derived system (not a service). The source and the first disconnect(s) will be in separate enclosures. I'd like to install the system bonding jumper in the transformer, outside, and run the supply side bonding jumpers to the disconnects (with the ungrounded conductors).
I remember an AHJ telling me once - probably related to a service - that the grounded conductor had to be brought to the first disconnect.
We are on the 2017 NEC and I do not see any requirement to bring the grounded conductor to the first disconnect for this installation. Am I correct? Besides - what would it do there, be ready in case someone needed it in the future?
Thanks!