Clayton502
Member
I recently inspected a building that had a new generator installed. The transfer switch switches the grounded conductor (neutral). The neutral and equipment grounding conductors are bonded at the generator and ground rods installed at the generator. Since this is a commercial building with a steel building frame I sited 250.30(4)1. Seems to me that with no solid neutral connection that the building steel or water pipe as in 250.30(4)2 must be used as the grounding electrode not the ground rods at the generator. The engineer for the job disagrees. Any opinions on this? Thank You