hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have 3MW generator three phase 480 V and all the loads that it’s feeding is three phase balanced load. This generator is standby and is feeding bunch of 3 phase chillers, 3 phase HVAC equipment for big building that has cell phone switch tenant. Note: This Generator Does NOT feed Fire Pump.
So there is three phase conductor and equipment going to the downstream ATS that is 4 poles.
Following questions:
1. Is neutral required to be brought in from the generator to the ATS per NEC 2014?
2. How can the separately derived generator be grounded and bonded if no neutral is brought based on NEC 2014 Section 250.30?
3. If anyone experience with this sort of thing how is generator grounded and bonded NEC 2014 Section 250.30?
Sent from my iPhone using Tapatalk
So there is three phase conductor and equipment going to the downstream ATS that is 4 poles.
Following questions:
1. Is neutral required to be brought in from the generator to the ATS per NEC 2014?
2. How can the separately derived generator be grounded and bonded if no neutral is brought based on NEC 2014 Section 250.30?
3. If anyone experience with this sort of thing how is generator grounded and bonded NEC 2014 Section 250.30?
Sent from my iPhone using Tapatalk