Can a separately derived system panel supply power to non-isolated ground receptacles.

[ July 15, 2003, 02:20 PM: Message edited by: bench892 ]
 

bennie

Esteemed Member
Re: separately derived system

Trace the equipment ground conductors from the receptacle to the service single point ground bus.

You will notice there is no other contact with a grounded object. The isolated ground is essentially an open circuit. No current will flow.

A non-isolated receptacle will have two ground points. This is a closed circuit; current will flow.

The isolated ground conductors should terminate at the ground electrode, not at the service panel neutral bus, but the code indicates it is approved to go to the bus.

There will be varying NE (neutral to earth) voltage on the neutral, this will create NE current.

I got a chance to try out my new terms. :p

[ June 19, 2003, 04:28 PM: Message edited by: bennie ]
 