BAHTAH
Senior Member
- Location
- United States
I install a 480-120/208 3ph4w transformer. Primary is either metallic conduit or PVC with EGC run from main service switchboard (where neutral and ground are bonded together) to transfomer. Transformer secondary neutral is bonded to the transformer enclosure and neutral. Is the metal conduit that is the EGC (250.118) or the EGC in PVC considered a solid connection of the transformer secondary Grounded Circuit Conductor to the primary system Grounded Circuit Conductor? Is this a Separately Derived System according to Art100?