electrofelon
- Cherry Valley NY, Seattle, WA
- Electrician
What they should have done is never created the concept of a "supply side connection". You already could do that using 230.40 exceptions. All they needed to do was tweak wording or provide an exception for the number of disconnects and grouping. They really made it silly and complicated.I still think it's funny that for the 20+ years I've been doing PV people have been arguing over if the supply side PV disconnect is/is not a service disconnecting means, and if not should it be installed under the same requirements anyway. The closest the NEC has been to defining this is the 2023 705.11(D) which calls the PV disconnect a service disconnecting means and requires that it be installed as a service disconnecting means. And that was only put in the 2023 NEC to stave off a code war with the CMP that covers 230 who wanted the disconnect to be considered a service disconnecting means and was willing to act on it by adding language to 230. But now that war has been averted the 2026 705.11 will remove the language. Massive changes in the code from cycle to cycle, always good for safety.
Grounding of supply side PV disconnects was defined in 2020 by the addition of 250.25. That was undefined for way too long.