Good afternoon I tried looking up the code for this response from an inspector so I can further educate myself by looking at 250.30, and 250.24 but just wanted to see if a grounding electrode conductor at my step down transformer is necessary (meter, transformer, and distribution panel are outdoors) even if my service main breaker panel and distribution panel have grounding electrode conductors already. According to the inspector it is not required at the transformer. Let me know if he is correct or if I do need a GEC at xfmr. Thanks in advance.
Inspector Response: “The Neutral-Ground bond occurs at the switchboard downstream of the transformer for the separately derived system so there would not be any ground rods or GEC at the delta-Wye transformer itself.”