Separately Derived Sytems

Status
Not open for further replies.

blues

Member
Location
Nevada
Per the attached sketch am I required to provide neutral to ground connections at each service feed from the utility transformer as shown. Also I am limited to the six switch rule for both services. In essence can I use the six switch rule for both services or is it a combination of both.
 

Attachments

  • E0.0 Symbols Legend & One Line Diagram (HLC4)-E0.1.pdf
    67.7 KB · Views: 0

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Per the attached sketch am I required to provide neutral to ground connections at each service feed from the utility transformer as shown. Also I am limited to the six switch rule for both services. In essence can I use the six switch rule for both services or is it a combination of both.

The 6 switch rule applies to each service. See 230.71(A).
 

dionysius

Senior Member
Location
WA
Per the attached sketch am I required to provide neutral to ground connections at each service feed from the utility transformer as shown. Also I am limited to the six switch rule for both services. In essence can I use the six switch rule for both services or is it a combination of both.
Answers to both questions:YES
 