To preface this, i have had an inspection fail before because the ground wires and neutral wires were not separated on isolated terminal bus within a panel before.
I have a main panel which is the service entrance of a dwelling unit, with a sub panel wired from it. There is no dedicated ground bus terminal in the main panel, all of the EGC, GEC and Neutral wires are terminated on the same common bus that also has the incoming service Neutral connected to it.
I understand that the service entrance needs to have a bonding jumper between the neutral and ground bus terminals;
, but there is no dedicated ground bus terminal in my main panel. Everything; service neutral, GEC to ground rod, EGC from branch circuits, Neutral from branch circuits, Ground bond to sub panel, Neutral bond to sub panel, are all terminated on the same neutral bus. And all of the GFCI breaker pigtails are also terminated on this same neutral bus as everything else.
First of all i dont believe that this is correct, despite that the service entrance needs a neutral → ground bonding jumper between the busses, but i also think this is why my GFCI breakers keep phantom tripping ALL THE TIME.
The GFCI pigtails should be terminated to the ground bus, NOT THE NEUTRAL BUS. Its detecting current and tripping because its terminated on the CURRENT CARRYING BUS.
Would like to know if i have this interpretation correct, thanks.
I have a main panel which is the service entrance of a dwelling unit, with a sub panel wired from it. There is no dedicated ground bus terminal in the main panel, all of the EGC, GEC and Neutral wires are terminated on the same common bus that also has the incoming service Neutral connected to it.
I understand that the service entrance needs to have a bonding jumper between the neutral and ground bus terminals;
, but there is no dedicated ground bus terminal in my main panel. Everything; service neutral, GEC to ground rod, EGC from branch circuits, Neutral from branch circuits, Ground bond to sub panel, Neutral bond to sub panel, are all terminated on the same neutral bus. And all of the GFCI breaker pigtails are also terminated on this same neutral bus as everything else.
First of all i dont believe that this is correct, despite that the service entrance needs a neutral → ground bonding jumper between the busses, but i also think this is why my GFCI breakers keep phantom tripping ALL THE TIME.
The GFCI pigtails should be terminated to the ground bus, NOT THE NEUTRAL BUS. Its detecting current and tripping because its terminated on the CURRENT CARRYING BUS.
Would like to know if i have this interpretation correct, thanks.