I'm wondering if, per 300.3, that I can have 480V pwr, 120V pwr, and 120V contacts in the same raceway.

I know the 480/120V pwr is ok together as long as the insullation is rated 600V, but I wasn't sure if the 120V relay contacts fell under the same boat (it would have 600V insulation as well).

Thanks.
 
You are correct, 300.3 permits 480 volt power, 120 volt power and a Class 1 120 volt control circuit to occupy the same raceway or enclosure provided that the voltage rating of the conductors is 600 V.

Chris
 
You are correct, 300.3 permits 480 volt power, 120 volt power and a Class 1 120 volt control circuit to occupy the same raceway or enclosure provided that the voltage rating of the conductors is 600 V.

Chris
Only if the Class 1 control circuit is "functionally associated" with the power conductors that are in the raceway.
 
I'm wondering if, per 300.3, that I can have 480V pwr, 120V pwr, and 120V contacts in the same raceway.

I know the 480/120V pwr is ok together as long as the insullation is rated 600V, but I wasn't sure if the 120V relay contacts fell under the same boat (it would have 600V insulation as well).

Thanks.

How are you putting contacts in a raceway? Are you talking about a wireway?
 
How are you putting contacts in a raceway? Are you talking about a wireway?

Was going to use a few homerun type multi-conductor TC cables in cable tray. The 120 V contacts are running/start/stop signals for devices (i.e. Motors), and 120V ESTOP contacts

Sorry misspoke when I said raceway.
 